Below you can find the detailed technical specification of the Touch Point series Wall Panels

Power Supply

DC20-34 V
AC24 V ± 20%
Power consumption0.5 W at 24 V DC, 0.75 VA at 24 V AC – up too 1 W peaks in max. configuration
Built-in Sensors








Temperature sensor10k NTC type, range: 0-50˚C, accuracy: ± 0.5˚C, resolution: ± 0.1˚C
Humidity sensor(applies to versions with humidity sensor)Range: 0-100% RH, accuracy: ± 2% RH in range 10-90% RH, resolution: ± 0.1% RH
CO2 sensor(applies to versions with CO2 sensor)Range: 400-4000 ppm, accuracy: ± 30 ppm
COM1RS485 interfaceUp to 128 devices
Half-duplex
Communication protocolsModbus RTU/ASCII, BACnet MS/TP
Ports2 RJ45, screw connector
Baud rate2400-115200
Front PanelSurfaceWhite/black glass
Display(applies to version with display)TFT 0.96″
Backlight3 intensity modes
Buttons5 (Touch Point series) / 3 (Touch Point VAV series)
LED3 blue and 3 red for temperature
3 white for fan (only the Touch Point series)
1 white for occupancy
1 configurable RGB
Ingress ProtectionIP ratingIP20 for indoor installation
Temperature

OperatingFrom 0°C to +40°C
StorageFrom -40°C to +70°C
HumidityRelativeFrom 5% to 95% RH (without condensation)
Screw Connector
TypeRemovable screw terminals
Maximum cable size1.5 mm2 (24…16 AWG)
HousingMaterialPlastic, self-extinguishing ABS
MountingStandard 60 mm wall back box
Dimensions

Metric86.00×86.00×14.50 mm
Inches3.39×3.39×0.57 in

Power Supply

Power supply can be provided through screw terminals or RJ45 connectors, making it a suitable option for connecting the panel to controllers that provide both power and communication through RJ45, like RAC18IP.

Communication

The same screw terminal and RJ45 connectors are used for the serial communication through BACnet MS/TP or Modbus RTU

USB Connection

The USB port is used to communicate with product software, such as the iSMA Configurator for configuration and firmware updates. The USB port provides 5 V DC power supply.

DIP Switch

There is a 3-position DIP Switch located under the back cover of the device.

Each of three sections has a separate function:

  1. Used for restoring default settings
  2. Communication protocol selection: 0 – Modbus, 1 – BACnet
  3. RS485 Termination – 0 – no termination, 1 – termination added (120 Ω)