Lesson Progress
0% Complete
Below you can find the detailed technical specification of the Touch Point series Wall Panels
| Power Supply | DC | 20-34 V |
|---|---|---|
| AC | 24 V ± 20% | |
| Power consumption | 0.5 W at 24 V DC, 0.75 VA at 24 V AC – up too 1 W peaks in max. configuration | |
| Built-in Sensors | Temperature sensor | 10k NTC type, range: 0-50˚C, accuracy: ± 0.5˚C, resolution: ± 0.1˚C |
| Humidity sensor(applies to versions with humidity sensor) | Range: 0-100% RH, accuracy: ± 2% RH in range 10-90% RH, resolution: ± 0.1% RH | |
| CO2 sensor(applies to versions with CO2 sensor) | Range: 400-4000 ppm, accuracy: ± 30 ppm | |
| COM1 | RS485 interface | Up to 128 devices |
| Half-duplex | ||
| Communication protocols | Modbus RTU/ASCII, BACnet MS/TP | |
| Ports | 2 RJ45, screw connector | |
| Baud rate | 2400-115200 | |
| Front Panel | Surface | White/black glass |
| Display(applies to version with display) | TFT 0.96″ | |
| Backlight | 3 intensity modes | |
| Buttons | 5 (Touch Point series) / 3 (Touch Point VAV series) | |
| LED | 3 blue and 3 red for temperature | |
| 3 white for fan (only the Touch Point series) | ||
| 1 white for occupancy | ||
| 1 configurable RGB | ||
| Ingress Protection | IP rating | IP20 for indoor installation |
| Temperature | Operating | From 0°C to +40°C |
| Storage | From -40°C to +70°C | |
| Humidity | Relative | From 5% to 95% RH (without condensation) |
| Screw Connector | Type | Removable screw terminals |
| Maximum cable size | 1.5 mm2 (24…16 AWG) | |
| Housing | Material | Plastic, self-extinguishing ABS |
| Mounting | Standard 60 mm wall back box | |
| Dimensions | Metric | 86.00×86.00×14.50 mm |
| Inches | 3.39×3.39×0.57 in |
Power Supply
Power supply can be provided through screw terminals or RJ45 connectors, making it a suitable option for connecting the panel to controllers that provide both power and communication through RJ45, like RAC18IP.
Communication
The same screw terminal and RJ45 connectors are used for the serial communication through BACnet MS/TP or Modbus RTU

USB Connection
The USB port is used to communicate with product software, such as the iSMA Configurator for configuration and firmware updates. The USB port provides 5 V DC power supply.
DIP Switch
There is a 3-position DIP Switch located under the back cover of the device.

Each of three sections has a separate function:
- Used for restoring default settings
- Communication protocol selection: 0 – Modbus, 1 – BACnet
- RS485 Termination – 0 – no termination, 1 – termination added (120 Ω)